Mudman57
Geotechnical
- May 27, 2004
- 6
I'm working on an electrical substation on a river estuary site in England. The ground investigation has found that the site is underlain by around 5m of pulverized fuel ash fill, over about 6m of alluvial soils, the top 3m of which is fibrous peat. Below the alluvium are river gravels and chalk. Water level appears to be below the peat layer, although this was only observed during drilling (the Client wouldn't pay for long term monitoring!)
Some background research suggests that the PFA fill was placed around the time of WWII, when an adjacent power station was constructed. The filling was intended to protect against flooding.
The PFA fill, even though it is lightweight, will obviously have caused consolidation in the peat, but due to the length of time since its placement, one would hope that most or all of the primary consolidation is complete, and a good deal of the secondary/creep.
The main substation structures are to be piled - i.e. the heavy transformers and switchroom. However the idea is that the smaller, lightweight ancillary structures are constructed on shallow foundations in the PFA (which the driller records as cemented, and had high SPT N values). Now this wouldn't give me too much concern, but for the fact it is also proposed to raise levels generally on the site by around 1.5-2m. I'm worried that this will set off new primary consolidation in the peat layer, with the result that the shallow founded structures could move excessively, not to mention of course that the external ground could settle away from the piled parts of the facility!
I have suggested the use of lightweight fill (further PFA for example) to mitigate this, but would welcome any thoughts on this from others.
I haven't posted before but have seen some very helpful posts and thought why not? I'm pretty much the only geotechnical engineer in my company and haven't got too much experience in dealing with peat. I know enough to be worried though!
Some background research suggests that the PFA fill was placed around the time of WWII, when an adjacent power station was constructed. The filling was intended to protect against flooding.
The PFA fill, even though it is lightweight, will obviously have caused consolidation in the peat, but due to the length of time since its placement, one would hope that most or all of the primary consolidation is complete, and a good deal of the secondary/creep.
The main substation structures are to be piled - i.e. the heavy transformers and switchroom. However the idea is that the smaller, lightweight ancillary structures are constructed on shallow foundations in the PFA (which the driller records as cemented, and had high SPT N values). Now this wouldn't give me too much concern, but for the fact it is also proposed to raise levels generally on the site by around 1.5-2m. I'm worried that this will set off new primary consolidation in the peat layer, with the result that the shallow founded structures could move excessively, not to mention of course that the external ground could settle away from the piled parts of the facility!
I have suggested the use of lightweight fill (further PFA for example) to mitigate this, but would welcome any thoughts on this from others.
I haven't posted before but have seen some very helpful posts and thought why not? I'm pretty much the only geotechnical engineer in my company and haven't got too much experience in dealing with peat. I know enough to be worried though!