jheidt2543
Civil/Environmental
- Sep 23, 2001
- 1,469
I’m looking at the interaction equation AISC (J3-3b), page 16.1-109, AISC Steel Manual, 13th Ed. solving for F’nt ? Fnt. For A325 bolts, Fnt = 90 ksi tension and Fnv = 48 ksi shear from AISC Table J3.2 and ? = 2.00 in ASD. This means that all the terms in equation J3-3b are constant except the shear stress fv.
If I have a connection that has both moment and shear and M = 118.5 ft-kips and V = 9.8 kips on a W14x38 (14.125” deep) then:
C = T = M/d = (118.5 x 12)/14.125 = 100.67 kips tension
this implies:
No. of bolts = T/Fnt = 100.67 kips/19.9 kips/bolt = 5.06 bolts
for shear:
No. of bolts = V/Fnv = 9.8 kips / 10.6 kips/bolt = .92 bolts
Choose five (5) bolts and check the interaction equation:
F’nt = 1.3*Fnt – (?*Fnt/Fnv)*fv ? Fnt = 1.3*90 – (2*90/48)*fv ? 90
For five (5) ¾” bolts fv = V/Ab = 9.8/(5*.442) = 4.43 ksi
Plugging this into the interaction equation:
1.3*90 – (2*90/48)*(4.43) ? 90 gives 100.4 ? 90
For seven (7) bolts 105.1 ? 90
For nine (9) bolts 107.8 ? 90
And for two (2) bolts 75.4 ? 90
How can fewer bolts be better???
Now there is a USER NOTE saying that if the tension or shear stress is LESS THAN 20% of the allowable we can ignore the combined effect. This only confuses me more, since I would think the formula should work in either case. Can someone point out what I’m missing?
If I have a connection that has both moment and shear and M = 118.5 ft-kips and V = 9.8 kips on a W14x38 (14.125” deep) then:
C = T = M/d = (118.5 x 12)/14.125 = 100.67 kips tension
this implies:
No. of bolts = T/Fnt = 100.67 kips/19.9 kips/bolt = 5.06 bolts
for shear:
No. of bolts = V/Fnv = 9.8 kips / 10.6 kips/bolt = .92 bolts
Choose five (5) bolts and check the interaction equation:
F’nt = 1.3*Fnt – (?*Fnt/Fnv)*fv ? Fnt = 1.3*90 – (2*90/48)*fv ? 90
For five (5) ¾” bolts fv = V/Ab = 9.8/(5*.442) = 4.43 ksi
Plugging this into the interaction equation:
1.3*90 – (2*90/48)*(4.43) ? 90 gives 100.4 ? 90
For seven (7) bolts 105.1 ? 90
For nine (9) bolts 107.8 ? 90
And for two (2) bolts 75.4 ? 90
How can fewer bolts be better???
Now there is a USER NOTE saying that if the tension or shear stress is LESS THAN 20% of the allowable we can ignore the combined effect. This only confuses me more, since I would think the formula should work in either case. Can someone point out what I’m missing?