Hi Fellows,
I'm working a project involving great distances from a main switchboard or power panel to some 250A 480/3 panels. The champion is an 850-foot run. In order to keep voltage drop to less than 3 percent, I calculated the need for 4 sets of 350 MCM per phase at an 80 percent load on the panel (200A) for this longest run.
My question is, I haven't found a 250A panel that can accept 4 x 350 MCM per phase at the main lugs, nor a switchboard breaker that can do so either. Do we need to spot a wiring box at each end to reduce the feeder size to "normal" (1 x 250 MCM) at each end?
Sorry for the elementary question -- I've just never run into these distances before. I've always been able to space my mains as needed to reduce feeder distances, but not in this cavernous building...
Thanks for your help!
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
I'm working a project involving great distances from a main switchboard or power panel to some 250A 480/3 panels. The champion is an 850-foot run. In order to keep voltage drop to less than 3 percent, I calculated the need for 4 sets of 350 MCM per phase at an 80 percent load on the panel (200A) for this longest run.
My question is, I haven't found a 250A panel that can accept 4 x 350 MCM per phase at the main lugs, nor a switchboard breaker that can do so either. Do we need to spot a wiring box at each end to reduce the feeder size to "normal" (1 x 250 MCM) at each end?
Sorry for the elementary question -- I've just never run into these distances before. I've always been able to space my mains as needed to reduce feeder distances, but not in this cavernous building...
Thanks for your help!
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies