Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Rebar Inspection

Status
Not open for further replies.

N3M4N

Structural
Aug 15, 2018
24
Hi all,

I would like to know the permissible gap between dowels out of footing and column vertical reinforcement?

Thanks
 
Replies continue below

Recommended for you

Depends on the design and your local code. Assuming a non-contact lap splice per ACI 318; spacing shall be between the minimum allowable clear spacing and the maximum of the lesser of 1/5 of the required lap splice length or 6 inches.

Ian Riley, PE, SE
Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries
 
and whether it was spec'd as a contact or not-contact splice.

Dik
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor