I didn't mean Miami Vice as some flippant comment. I meant it as a sort of oblique comment regarding people's judgement being affected, and the quality of design in Florida in the 1980s that I've seen documented. I meant don't take anything as a given that it's properly designed, particularly if you have actual construction drawings. Missing rebar, terrible inspections, etc. To say nothing of poor design and people not bothering to check their work.
How these hypothetically defective structures get ammended is on us, as the living engineers. Life safety and welfare. If you can't figure out how to reinforce it, I think that's "fine" so long as you can produce a coherent report that will allow another engineer to undertake the work (after confirming you're not a wingnut).
Where does the line get drawn between this is a) defective b) dangerous, c) hazardous d) wrong but fine and e) evacuate now, get drawn? That I don't know. It depends on each individual engineer and what their decision making process is. I'll point at Davenport, Iowa, however. Clearly at least some engineers can't see a hazard, or won't. New York City is another example. At least one South Florida condo was evacuated and extensive repairs to the loadbearing columns was performed. I won't name it, because the other one the guy looked at got minimal repairs and collapsed.
Going back to the Miami Vice comment, corridors are exit ways. Horizontal exit ways, transfer corridors, whatever you want to call them.
Corridors, the way a lot of these places are designed, the first floor is pretty public, and it's already 100 psf as a first floor corridor. The upper floors I see a lot of folks wanting to use quite a bit less, it doesn't do much for the column design on a multi-story building one way or the other, and in a concrete building it's pretty impractical to reduce the depth if the live load is 40 versus 100, only for the corridor, and I'll stand by the 100 psf. I've seen projects kicked back by more rigorous building departments for using 40 psf in a "private corridor" in a hotel when it's actually for accessing the rooms from the public elevator and the egress stairs. A private corridor is inside a private room.
That doesn't mean that some yahoo engineer didn't design something in 1980 for 40 psf live load and nobody bothered to review it, or for that matter, file the drawings. It isn't all that realistic for, say, a hotel corridor to experience 100 psf, but that's what the code (life safety) calls for, as I've seen it interpreted, so if you're evaluating a design, I think you have to expect all of it to be done wrong and then work to disprove that assumption via generally accepted principles of mechanics and structural analysis and the code in place at the time of construction/design.
It's fairly likely a 33 story concrete building that was designed incorrectly (quotation marks deliberately not provided) for 40 psf exit ways wouldn't be gravely affected by this error (provided you even agree with me on 100 psf, which I rather doubt).
People design stuff for forty years (or twenty) and somebody comes along and asks a question and there's no possible way the other person has been doing it wrong for twenty or forty years, so it gets discarded. Ego protection. Or you get the "ultimately it won't matter" hand waving argument and no calculations. It's fine to disagree, but the hand-wave is what I dislike, if it doesn't matter, put down the calculations SHOWING that. It reminds me of the old "design for 10 psf net uplift" notes I'd see on steel joist framing plans. There's never a calculation showing that 10 psf applies (and it can fairly often be inadequate, the structure just happens to not see the design wind speed, SO FAR).
Some of these checks are exceedingly easy to perform, like checking percent reinforcement in a concrete column, the floor strength/column strength limit, the minimum depth to ignore deflections in a two-way slab, this is all so trivially easy to do and you look at Harbour Cay and Champlain Towers South and all three of these items are a fail.
When stuff this basic cannot be depended on being done correctly, the entire structure must be viewed with extreme skepticism. Admittedly, Harbour Cay was designed by two people with, I believe, literally no training or education in the field of concrete design, but it isn't like these checks are somehow not in the code if you read it from cover to cover. It's all there in the printed sections, written with visible ink. No secret decoder ring needed. You would think somebody with zero design experience would be MORE literal with the code, not less. And yet, no.