Part 1:
I often see CMU jambs, located between large window and door openings, being constructed with (1)#5 bar centered in each cell for (2) or (3) cells.
Let's say you have (2) filled cells side by side acting as your wind jamb, w/(1)#5 bar centered in each cell of an 8" unit. Treating this shape (8" x 16") as a flexural element, this provides ρ = As/bd = (2)0.31in²/[16in x 3.8125in] = 0.0101
TMS 602-16 / ACI 530.1 limits flexural elements to ρmax = 0.286 f'm/fy.
For f'm=1500 psi and fy=60,000 psi, ρmax = 0.00715, which is less than 0.0101.
So what gives here? Is this jamb "over reinforced"? This error came up in Enercalc while trying analyze a wall for a 16" strip (ie, 2 filled cells)
Part 2:
I've seen this debated before and have not found a consensus. In a situation as described above, utilizing the jamb for combined lateral and gravity, does the jamb constitute a column or some other structural element (pilaster). How do you handle this design?
I often see CMU jambs, located between large window and door openings, being constructed with (1)#5 bar centered in each cell for (2) or (3) cells.
Let's say you have (2) filled cells side by side acting as your wind jamb, w/(1)#5 bar centered in each cell of an 8" unit. Treating this shape (8" x 16") as a flexural element, this provides ρ = As/bd = (2)0.31in²/[16in x 3.8125in] = 0.0101
TMS 602-16 / ACI 530.1 limits flexural elements to ρmax = 0.286 f'm/fy.
For f'm=1500 psi and fy=60,000 psi, ρmax = 0.00715, which is less than 0.0101.
So what gives here? Is this jamb "over reinforced"? This error came up in Enercalc while trying analyze a wall for a 16" strip (ie, 2 filled cells)
Part 2:
I've seen this debated before and have not found a consensus. In a situation as described above, utilizing the jamb for combined lateral and gravity, does the jamb constitute a column or some other structural element (pilaster). How do you handle this design?