Reinforcement details around large openings in slabs 1

Status
Not open for further replies.

Amr Abdelhalim

Structural
May 12, 2019
12
0
0
EG
I need help in reinforcement details around large openings in RC slabs, I am aware that ACI 318 states that the removed reinforcement by the opening is to be put on each side of the opening. The problem here that I have large openings (1m x 2m) due to mechanical requirements inside a slab of thickness 1m, I don't think only replacing removed rebars on each side is right in such case, I need some resources in dealing with such large openings, thanks.
 
Replies continue below

Recommended for you

Design the slab as a series of strips. Take about 1 meter wide strips each side of the opening. Each strip is designed like a one way slab or beam. The header strips are designed to span to the centre line of each of the perpendicular strips.
 