I need help in reinforcement details around large openings in RC slabs, I am aware that ACI 318 states that the removed reinforcement by the opening is to be put on each side of the opening. The problem here that I have large openings (1m x 2m) due to mechanical requirements inside a slab of thickness 1m, I don't think only replacing removed rebars on each side is right in such case, I need some resources in dealing with such large openings, thanks.
 
Replies continue below

Recommended for you

You might consider using Yield Line Analysis (upper bound) or the Hillerborg Strip Method (lower bound).

BA
 
Design the slab as a series of strips. Take about 1 meter wide strips each side of the opening. Each strip is designed like a one way slab or beam. The header strips are designed to span to the centre line of each of the perpendicular strips.
 