atrizzy
Structural
- Mar 30, 2017
- 362
I have a situation where I have a W460 steel transfer beam that has undergone significant corrosion, to the point where the web is too slender to function (thickness testing is currently ongoing). Flange flexural capacity is still OK. Replacing this beam is almost impossible as it supports structure above, as well as beams framing into it. I've had the following thoughts on fixing this:
1. Add web stiffeners at the appropriate spacing to mimic a compact web. The issue here is that the web may well be too thin to weld to.
2. (more out of the box) Ignore the web entirely, treat the flanges as truss chords, and provide diagonal and vertical stiffeners (angles even) capable of resisting the forces in a truss analysis. This will require a bit of fancy detailing around the beams framing into... but I think it's doable.
Any thoughts about my ideas above, or other thoughts?
1. Add web stiffeners at the appropriate spacing to mimic a compact web. The issue here is that the web may well be too thin to weld to.
2. (more out of the box) Ignore the web entirely, treat the flanges as truss chords, and provide diagonal and vertical stiffeners (angles even) capable of resisting the forces in a truss analysis. This will require a bit of fancy detailing around the beams framing into... but I think it's doable.
Any thoughts about my ideas above, or other thoughts?