Relay pick up current

Status
Not open for further replies.

Fazlay

Electrical
Sep 9, 2018
15
As far i know for a protection relay,
Pick up current (Min Trip Current) = CT ratio × PSM (plug setting)

According to this formula,For below information i got 68A pick up current. Is this correct?
IMG_20181208_225525_explgk.jpg
 
Replies continue below

Recommended for you

400A CT with a 0.85 plug setting would give 340A pickup.
 
Sorry Scotty, I gotta go with the 68A. This is a 5A secondary CT, CTR = 80. The setting would be in secondary amps, so 80 * 0.85 = 68A. At 400:1 I'd agree with your 340A.
 
David - yes of course. Too long in the world of 1A CT's - don't see so many 5A's these days. Sorry Fazlay. [blush]
 
[smile] it's ok Mr.Scotty. 5A CT's are really rare these days compare to 1A CT
 
5A CTs are far from rare. I don’t think I’ve ever even seen a 1A CT. Another one of those ANSI v. IEC things.
 