Relief capacity conversion
JBombard
Chemical
Apr 28, 2009
1
I am looking to size a PRV for a propane cylinder and have run into a snag that my simple mind can't seem to get past. The NFPA code calculation gives an answer in lb/hr but the relief valves are certified in SCFM of free air. I can get to SCFM of propane without issue but how does one compare propane to air?
Thank you for any insight.
Jason
ASME Section VIII, Division 1, Appendix 11 explains how to perform capacity conversions for pressure safety valves. If you don't have the ASME code you can find an excerpt in the Crosby Engineering Handbook...
Also, don't overlook contacting a local valve supplier. I'm sure they would be happy to assist.
I use the following
SCFM (air)= (flow x 13.36)/(SG x (1/SG)^.5)
where
flow= flow rate of propane in lb/minute
and SG= specific gravity of propane
density of gas = density of air x specific gravity of gas
If it's a PRV I'd go with the method in Appendix 11, since it's what the vendors will have to go by to certify the capacity of the valve (provided it's an ASME UV valve).