Hi,
I am designing a relief system for a gas dehydration station, the equipment handling high pressure gas are the well separator receiving the well stream, the inlet dehydration scrubber, the glycol contactor and the outlet dehydration scrubber. All of these equipment will have installed relief valves with the same set point.
In the case of a blocked outlet downstream the glycol contactor, the pressure will rise in all the system, but the first relief valve opened will be the one of the well separator, after, the one of the inlet scrubber and so on.
Taking this into account, it is not probable that the relief load of the outlet scrubber or the glycol contactor will be the total flow rate passing through the vessel, it will be lower because it is relieving in the first relief valves.
In the case of blocked outlet, API 521 recommends to size the PSV to be able to relief all the flow rate normally passing through the vessel.
In this case, API 521 recommendation is not applicable (considering the facts), how can I determine the maximum relief load from each source, taking into account the pressure profile along the station.
I appreciate the help you can give me.
I am designing a relief system for a gas dehydration station, the equipment handling high pressure gas are the well separator receiving the well stream, the inlet dehydration scrubber, the glycol contactor and the outlet dehydration scrubber. All of these equipment will have installed relief valves with the same set point.
In the case of a blocked outlet downstream the glycol contactor, the pressure will rise in all the system, but the first relief valve opened will be the one of the well separator, after, the one of the inlet scrubber and so on.
Taking this into account, it is not probable that the relief load of the outlet scrubber or the glycol contactor will be the total flow rate passing through the vessel, it will be lower because it is relieving in the first relief valves.
In the case of blocked outlet, API 521 recommends to size the PSV to be able to relief all the flow rate normally passing through the vessel.
In this case, API 521 recommendation is not applicable (considering the facts), how can I determine the maximum relief load from each source, taking into account the pressure profile along the station.
I appreciate the help you can give me.