Hello engineers!
As I understand, to avoid chattering, there is a limit of allowable pressure drop for relief valve inlet and discharge lines. My queries & understanding is summarised as below.
1) I believe, inlet pressure drop is always 3% of set pressure which is independent of overpressure. Please correct me if I am wrong.
2) However, discharge line pressure drop depends on overpressure i.e. generally we allow 21% overpressure fire case and other process upset conditions we allow 10% overpressure.
• I believe, if I design a valve for fire case allowing 21% overpressure, am I correct that the allowable overpressure at the valve discharge line is 21%?
• And therefore, if the overpressure is 10%, am I correct that the valve discharge line allowable pressure drop is 10%?
3) Also, I have one query for one specific example
If the design pressure of the vessel is 10barg and the relief valve is installed independently at set pressure of 5barg [please note that the set pressure of valve is quite less compared to the design pressure]. I am designing it for the external fire and process upset conditions. Please advise what overpressure should I allow for external fire case and process upset case?
Thank you very much.
KS
As I understand, to avoid chattering, there is a limit of allowable pressure drop for relief valve inlet and discharge lines. My queries & understanding is summarised as below.
1) I believe, inlet pressure drop is always 3% of set pressure which is independent of overpressure. Please correct me if I am wrong.
2) However, discharge line pressure drop depends on overpressure i.e. generally we allow 21% overpressure fire case and other process upset conditions we allow 10% overpressure.
• I believe, if I design a valve for fire case allowing 21% overpressure, am I correct that the allowable overpressure at the valve discharge line is 21%?
• And therefore, if the overpressure is 10%, am I correct that the valve discharge line allowable pressure drop is 10%?
3) Also, I have one query for one specific example
If the design pressure of the vessel is 10barg and the relief valve is installed independently at set pressure of 5barg [please note that the set pressure of valve is quite less compared to the design pressure]. I am designing it for the external fire and process upset conditions. Please advise what overpressure should I allow for external fire case and process upset case?
Thank you very much.
KS