Here's what I've got: Tank MAWP = 430 psig; Existing PSV set pressure = 420 psig; Critical Pressure of contents (F-404a) = 541.2 psia; Sizing Scenario = Fire Case (F-404a is not flammable, but client wants to see the calcs).
OK, so here's my question: How is the relieving pressure calculated when the set pressure < MAWP? The reason this matters is because it affects the value for the heat of vaporization of F-404a that we "plug" into the sizing equations. A lower relieving pressure means we get away from the critical pressure, get a larger value for heat of vaporization, and this allows us to use a smaller valve.
I'm pretty sure the relieving pressure in this case is either 535 psia (based on MAWP) or 522.9 psia (based on set pressure), there's not really that much of a difference. However, the suggestion was made to lower set pressure to 350 psig in order to lower relieving pressure to 438.2 psia. Now there's quite a bit of difference.
In my mind, relieving pressure should be based on set pressure, but API 520, 8th ed., Tables 2 thru 6 destroyed that idea. In their examples, relieving pressure is exactly the same, no matter if set pressure is equal to MAWP or set pressure is less than MAWP.