Ron,
Yes, so the single member is used for a straight up single 2x member that violates the requirements for repetitive member. But up here we call repetitive member "System Cases" where our increase is 40% over a stand-alone single joists however this is subject to a minimum of 3/8" board sheathing or 5/8" decking to qualify(i.e. System case 2).
That being said, we also have System Case 1 members in the joist design area that indicates
"Case 1 systems are composed of three or more essentially parallel members spaced no more than 24" apart and are arranged so they mutually support the load. However, Case 1 systems lack the sheathing and fastening requirements to qualify as Case 2 systems; or they may include a more complex structural component such as a wood truss." Which when you go on to read it says if you qualify for case 1 but not case 2, you multiple the single member values by 1.10. so there may be some validity to applying to beams.
What I was saying is when comparing the capacity of 2, 3, 4, and 5 ply
beams to the single member capacity there is a 10% increase over just taking the single member capacity and multiplying by 2, 3, 4 or 5.
In the Canadian code however, Mr is a function of bending stress, section modulus, and two factors Kz (Size factor) and KL (Lateral stability factor). Digging deeper, it appears they apply the 1.1 factor to the bending stress for beams prior to publishing the number. So we never see a "repetitive member factor" in our beam design formulae if you just pick the beam bending stress from the tables.
Long winded story cut short (TL;DR), In Canada even 2 ply beams have a repetitive member factor included, however it is only a 10% increase for all built up beams. The repetitive member factor for joists with floor sheathing is a 40% increase.
KootK said:
On the other-hand, Jayrod12 is our reigning tip-master / demigod of the week. So there's that.
Twice in my tenure, and I'm pretty sure I just got lucky.
edited for clarity