I've done a fan test for a automatic fire extinguishing system with IG55 following the NFPA 2001, appendix C, enclosure integrity procedure.
Given that it is not possible to lower the amount of leak areas, how can I adjust the design to have a functional extinguishing system?
A secondary flooding is the only possibility I think. But how can I calculate the hold time and concentration after 10 min with a secondary flooding. I cannot find anything in NFPA 2001 nor CEO 4007.
Any help?
*edit
Known data
CO2 quantity: 22,8 kg
Real concentration: 43%
Volume room: 29 m³
Max height room: 3,25 m
Minimal concentration: 38%
Temperature in the room: 21°C
Temp outside: 21°C
CO2 quantity: 22,8 kg
Real concentration: 43%
Volume room: 29 m³
Max height room: 3,25 m
Minimal concentration: 38%
Temperature in the room: 21°C
Temp outside: 21°C
The results aren't good:
Surface area leaks: 0,0592 m²
Max accepted surface area leaks: 0,0128 m²
Hold time: 2 min 10 sec
Concentration after 10 min: 22,2%
Surface area leaks: 0,0592 m²
Max accepted surface area leaks: 0,0128 m²
Hold time: 2 min 10 sec
Concentration after 10 min: 22,2%
Given that it is not possible to lower the amount of leak areas, how can I adjust the design to have a functional extinguishing system?
A secondary flooding is the only possibility I think. But how can I calculate the hold time and concentration after 10 min with a secondary flooding. I cannot find anything in NFPA 2001 nor CEO 4007.
Any help?
*edit