AZengineer
Structural
- Apr 3, 2005
- 46
I know a lot of questions have been posted on this topic, but I still am unable to see a popular consensus:
I have a very long rectangular building with a full basement (10' ceiling). There are no intermediate walls perpendicular to the long direction. The floor trusses run parallel to the long dimension of the building, with steel beams spaced at about 25' o.c.
Since the basement is backfilled on all sides, I would like to design the walls as restrained masonry walls, and the contractor would obviously like to avoid the extra expense of a cantilevered wall. The geo report specifies the at-rest pressure as 63 pcf, which gives a lateral reaction of roughly 1000 plf into the floor sheathing.
I cannot justify the load transfer at an interior sheathing panel joint. I am able to justify the load transfer through the bearing plate/ledger into the sheathing via blocking, but that's where I run into problems. The APA recommends a 1/8" gap between sheathing panels, which means that 1000 plf will have to be transferred across this joint by the sheathing nails/screws. I am also slightly concerned about plywood buckling under axial load, since the tabulated values in the NDS assume all edges are restrained, whereas in my case the floor trusses are spaced at 24" o.c.
I have seen many designs where a 10' basement wall is designed as a restrained wall, and many engineers extend blocking several truss bays to get the load into the sheathing, using the IBC diaphragm shear values - which is not correct - this is not a diaphragm, rather an axially loaded plywood floor. Nevertheless, this design has been employed on many local projects (Phoenix, AZ), and seemingly without problems.
Any suggestions on how to justify this? I would like to avoid putting blocking in all the way across the building, as this is not a realistic solution when shrinkage and workmanship are taken into account.
I have a very long rectangular building with a full basement (10' ceiling). There are no intermediate walls perpendicular to the long direction. The floor trusses run parallel to the long dimension of the building, with steel beams spaced at about 25' o.c.
Since the basement is backfilled on all sides, I would like to design the walls as restrained masonry walls, and the contractor would obviously like to avoid the extra expense of a cantilevered wall. The geo report specifies the at-rest pressure as 63 pcf, which gives a lateral reaction of roughly 1000 plf into the floor sheathing.
I cannot justify the load transfer at an interior sheathing panel joint. I am able to justify the load transfer through the bearing plate/ledger into the sheathing via blocking, but that's where I run into problems. The APA recommends a 1/8" gap between sheathing panels, which means that 1000 plf will have to be transferred across this joint by the sheathing nails/screws. I am also slightly concerned about plywood buckling under axial load, since the tabulated values in the NDS assume all edges are restrained, whereas in my case the floor trusses are spaced at 24" o.c.
I have seen many designs where a 10' basement wall is designed as a restrained wall, and many engineers extend blocking several truss bays to get the load into the sheathing, using the IBC diaphragm shear values - which is not correct - this is not a diaphragm, rather an axially loaded plywood floor. Nevertheless, this design has been employed on many local projects (Phoenix, AZ), and seemingly without problems.
Any suggestions on how to justify this? I would like to avoid putting blocking in all the way across the building, as this is not a realistic solution when shrinkage and workmanship are taken into account.