Bloozntooz7868
Electrical
- May 23, 2014
- 27
I am trying to make sense of currents I am seeing on 2 parallel incomers to a switchboard. We have a 480V Emergency Board with a main incomer from our grid (made up of 9 Turbine Generators), and a Diesel Generator (DG) incomer with a rated power of 1310kW. The intention is that if normal power is lost the diesel Gen supplies the board to power essential supplies.
Operations perform a weekly test on the DG and run it in parallel with the main for a 4 hour load run. When in parallel the system is configured to run the DG at rated power (1310kW) with a PF of 0.99 (of course, when in stand-alone operation, it will supply the demand of the load). It does this automatically with a 2.5 minute loading ramp (soft load), and a 1.5 minute off-loading ramp. The system works without any flaws.
Observing the currents on both the incomer Cutler-Hammer circuit breaker (which have inbuilt Digitrip protection relays that show phase current) during the loading and unloading sequences, I see values that I am having some trouble understanding:
1) With the main breaker only closed (grid supplying the board), I observe phase current of 1330A on the relay. This more or less equals the summation of the outgoing load breakers (which also have Digitrip units). No problem there.
2) With the DG running in parallel I observe phase currents of 1600A on DG incomer (more than the load requirement), but yet 710A on Main incomer. It is this that I am trying to understand and I believe it is to do with the PF 0.99 that the DG is forced to run at, while in parallel with a system that has its own dynamic PF based on the wider load.
Some round figure calculations:
3) The phase current (via the main breaker) of the Emergency Board is 1330A. Neglecting any imbalance, and assuming a PF of 0.9 (we do not have the ability to check P, Q, S, or PF on the board) this equates to 980KW and 483KVAr actual load.
4) With the DG running in parallel, the DG incomer shows 1600A phase current at PF 0.99, which equates to 1317KW (which tallies with the rated output of 1310KW) and 188KVAr.
5) Again, with the DG running in parallel, the main incomer shows 710A which equates to 531KW and 260KVAr (this is my problem area)
6) The resultant of the load demand (from point 3) and the ‘supplied’ DG values (from point 4) is: 980KW-1317KW = -337KW and 483KVar-188KVar = +295KVAr
I would assume that the -337KW would be the real power export back to the grid, and the +295KVAr would be the required reactive power import from the grid (due to the DG running at 0.99PF and not fully supporting excitation requirements)?
Q1) So how come I am seeing 710A phase current on the main incomer breaker? This equates to (again using system 0.9PF) 531KW and 260KVAr (the Digitrip relays on the breakers do not recognise direction so I am not able to determine if this current value is import or export).
Q2) How can I determine resultant currents when I have an export of real power but an import of reactive power?
The only figures I see that are close are the 260KVAr main incomer reactive power calculation (from point 5) that is near to the calculated requirement of 295KVAr (from point 6) that the loads on the board need.
I may be looking at this all wrong so all help is appreciated, and thanks in advance for your time responding.
Operations perform a weekly test on the DG and run it in parallel with the main for a 4 hour load run. When in parallel the system is configured to run the DG at rated power (1310kW) with a PF of 0.99 (of course, when in stand-alone operation, it will supply the demand of the load). It does this automatically with a 2.5 minute loading ramp (soft load), and a 1.5 minute off-loading ramp. The system works without any flaws.
Observing the currents on both the incomer Cutler-Hammer circuit breaker (which have inbuilt Digitrip protection relays that show phase current) during the loading and unloading sequences, I see values that I am having some trouble understanding:
1) With the main breaker only closed (grid supplying the board), I observe phase current of 1330A on the relay. This more or less equals the summation of the outgoing load breakers (which also have Digitrip units). No problem there.
2) With the DG running in parallel I observe phase currents of 1600A on DG incomer (more than the load requirement), but yet 710A on Main incomer. It is this that I am trying to understand and I believe it is to do with the PF 0.99 that the DG is forced to run at, while in parallel with a system that has its own dynamic PF based on the wider load.
Some round figure calculations:
3) The phase current (via the main breaker) of the Emergency Board is 1330A. Neglecting any imbalance, and assuming a PF of 0.9 (we do not have the ability to check P, Q, S, or PF on the board) this equates to 980KW and 483KVAr actual load.
4) With the DG running in parallel, the DG incomer shows 1600A phase current at PF 0.99, which equates to 1317KW (which tallies with the rated output of 1310KW) and 188KVAr.
5) Again, with the DG running in parallel, the main incomer shows 710A which equates to 531KW and 260KVAr (this is my problem area)
6) The resultant of the load demand (from point 3) and the ‘supplied’ DG values (from point 4) is: 980KW-1317KW = -337KW and 483KVar-188KVar = +295KVAr
I would assume that the -337KW would be the real power export back to the grid, and the +295KVAr would be the required reactive power import from the grid (due to the DG running at 0.99PF and not fully supporting excitation requirements)?
Q1) So how come I am seeing 710A phase current on the main incomer breaker? This equates to (again using system 0.9PF) 531KW and 260KVAr (the Digitrip relays on the breakers do not recognise direction so I am not able to determine if this current value is import or export).
Q2) How can I determine resultant currents when I have an export of real power but an import of reactive power?
The only figures I see that are close are the 260KVAr main incomer reactive power calculation (from point 5) that is near to the calculated requirement of 295KVAr (from point 6) that the loads on the board need.
I may be looking at this all wrong so all help is appreciated, and thanks in advance for your time responding.