asabender
Structural
- Feb 8, 2013
- 28
I have been trying to check an uplift scenario for a finish-work installing client. In this case, they are trying to put terrace patio pavers on a high rooftop in a hurricane prone region. The IBC specifically says that aggregate is not allowed on roofs, and that ballasted roofs are not allowed in this application (1504.8). The roof isn't ballasted (it's structural, this is just a wearing surface) and ANSI/SPRI RP-4 specifically reference 22psf or greater pavers (which we are) as an alternative to ballast stone (RP-4-4.1.3.1), so one could infer that we are in line with IBC, so long as we meet the uplift requirements of ASCE 7 on the pavers. My first question is just, "Does anyone see a major problem with that logic?" Obviously, it has to be designed so that a bunch of concrete squares don't go a-killin' in the next hurricane.
Assuming pavers on roofs are generally copacetic, IBC has a specific requirement for "ridgid tile", which includes concrete, under 1609.5.3. This code basically says that uplift is qh*Cl where Cl is .2 for concrete, then goes on to use it in an overturning calculation. The code also says that I have to be in accordance with ASCE 7 ch 6 (1609.1.1). ASCE says that components and cladding are basically qh*GCp (since GCpi=n/a); since it's a stepped flat roof, GCp should be from 6-12&6-11b as required. ASCE 7 could also be read as allowing the blocks as "other structures", which would make sense to me, since they aren't fixed to the building. Following these methods, and going with the worst case, I'm killing them in zone 3, and really making life hard in zone 2.
At my request, my client has provided parapet information. The parapet is more than 3 feet tall (usually 5), is designed sturcturally by others, and SHOULD have a large effect on suction since my maximum height is something like 300 feet. All the research that I have read shows large decreases in zone 3 and decreases in zone 2, but I can't find anything in ASCE 7, which is, in this case, IBC's go to guy (and, in general I would agree that it is the book to use... but where is the effect of the parapet?!). Does anyone know how to take the parapets into account?
Finally, the code combinations dictate that I use .6D, which I'm all for in a structure where design dead load is conservative and loads may vary, but these are pre-cast blocks with dependable weights and no room for variation. Gravity will not get weaker during the hurricane. Does anyone know if, in a case like this, .6D is still a requirement?
Assuming pavers on roofs are generally copacetic, IBC has a specific requirement for "ridgid tile", which includes concrete, under 1609.5.3. This code basically says that uplift is qh*Cl where Cl is .2 for concrete, then goes on to use it in an overturning calculation. The code also says that I have to be in accordance with ASCE 7 ch 6 (1609.1.1). ASCE says that components and cladding are basically qh*GCp (since GCpi=n/a); since it's a stepped flat roof, GCp should be from 6-12&6-11b as required. ASCE 7 could also be read as allowing the blocks as "other structures", which would make sense to me, since they aren't fixed to the building. Following these methods, and going with the worst case, I'm killing them in zone 3, and really making life hard in zone 2.
At my request, my client has provided parapet information. The parapet is more than 3 feet tall (usually 5), is designed sturcturally by others, and SHOULD have a large effect on suction since my maximum height is something like 300 feet. All the research that I have read shows large decreases in zone 3 and decreases in zone 2, but I can't find anything in ASCE 7, which is, in this case, IBC's go to guy (and, in general I would agree that it is the book to use... but where is the effect of the parapet?!). Does anyone know how to take the parapets into account?
Finally, the code combinations dictate that I use .6D, which I'm all for in a structure where design dead load is conservative and loads may vary, but these are pre-cast blocks with dependable weights and no room for variation. Gravity will not get weaker during the hurricane. Does anyone know if, in a case like this, .6D is still a requirement?