structuresguy
Structural
- Apr 10, 2003
- 505
A question has come up on how to design nailing patterns for roof plywoood, considering combined interaction of uplift loads and diaphragm shear. I have typically done a linear interaction of tension/shear for fasteners, but can't find any direct language to this interaction for engineered panels. Basically, if I use the APA tables for allowable horizontal diaphragm nailing, and want to also consider nail withdrawal for simutaneous uplift loads, what is the best way to calculate this interaction? There is an equation in NDS for interaction with nails, but it is based on individual nail capacities, not engineered panel capacities.
So I am thinking to calculate the number of nails in a 4x8 sheet of plywood, based on the diaphragm capacity tables, then work out the total uplift on that 4x8 sheet, then using the withdrawal capacity of each nail, calculate the total allowable uplift load based on the number of nails. Then I could do a linear (or otherwise) interaction of the withdrawal tension and diaphragm shear. This is the same approach we use for metal deck fastening patterns. What do you think?
Thanks very much.
So I am thinking to calculate the number of nails in a 4x8 sheet of plywood, based on the diaphragm capacity tables, then work out the total uplift on that 4x8 sheet, then using the withdrawal capacity of each nail, calculate the total allowable uplift load based on the number of nails. Then I could do a linear (or otherwise) interaction of the withdrawal tension and diaphragm shear. This is the same approach we use for metal deck fastening patterns. What do you think?
Thanks very much.