caseypoi23
Structural
- Jul 26, 2016
- 11
i'm designing an HSS platform on a concrete roof. the platform supports two AC units, and the platform consists of beams which span to short HSS posts. the columns are anchored to the concrete roof slab, over concrete columns (the slab and beams cannot support the AC/platform dead loads). the platform also has grating to support maintenance workers. platforms about 2' high.
i'm designing the anchorage of the units to the platform with Fp determined from asce 7-10 chapter 13, with internally isolated components (Fp = 2.44 * W). also checking the platform beams for these loads.
question:
when anchoring the platform itself to the concrete roof... should i still use the 2.44 * W? seems overkill, although that's what the load path would come down to... also, i'd have to use omega on the anchorage to the roof, which will kill the design. i'm pretty sure this is the case, but would love to hear thoughts on this.
thanks y'all.
i'm designing the anchorage of the units to the platform with Fp determined from asce 7-10 chapter 13, with internally isolated components (Fp = 2.44 * W). also checking the platform beams for these loads.
question:
when anchoring the platform itself to the concrete roof... should i still use the 2.44 * W? seems overkill, although that's what the load path would come down to... also, i'd have to use omega on the anchorage to the roof, which will kill the design. i'm pretty sure this is the case, but would love to hear thoughts on this.
thanks y'all.