bob090470
Specifier/Regulator
- Apr 5, 2007
- 2
I'm working with an Owner that is having humidity problems in an existing office building (small - 5000sf sigle-story office in Florida). Office currently has two RTU's, one serving an interior zone and one a perimeter zone. Both units share a common plenum for return. To be specific, each unit is a Trane Model WCD075C400BC.
I work in construction (so please excuse my basic understanding of unit operation) and rely on engineers and contractors for input, but in this case I can't seem to get a straight answer. I'm really just wondering about the basic operation of units like these. It seems to me that diagnosing the humidity problem requires an understanding of how these units operate.
Is the OA damper fixed on units like this, or do we have the ability to open it during occupied mode and close it during unoccupied mode?
During occupied mode, I assume the coil shuts down when space temperature is satisfied, but does the fan continue to run to meet OA requirements (filling the space with humid outside air)? If so, would it be OK to limit fan operation to only when cooling is called for?
During unoccupied mode, since we don't have to meet OA requirement, I assume it would be OK to only run the fan during cooling? I also assume it would be OK to close OA damper (assuming it's motorized)?
If closing the damper or limiting fan operation aren't options, how the heck can you control humidity with units like these?
I work in construction (so please excuse my basic understanding of unit operation) and rely on engineers and contractors for input, but in this case I can't seem to get a straight answer. I'm really just wondering about the basic operation of units like these. It seems to me that diagnosing the humidity problem requires an understanding of how these units operate.
Is the OA damper fixed on units like this, or do we have the ability to open it during occupied mode and close it during unoccupied mode?
During occupied mode, I assume the coil shuts down when space temperature is satisfied, but does the fan continue to run to meet OA requirements (filling the space with humid outside air)? If so, would it be OK to limit fan operation to only when cooling is called for?
During unoccupied mode, since we don't have to meet OA requirement, I assume it would be OK to only run the fan during cooling? I also assume it would be OK to close OA damper (assuming it's motorized)?
If closing the damper or limiting fan operation aren't options, how the heck can you control humidity with units like these?