jscaufi
Electrical
- Sep 8, 2003
- 13
I have been asked a question by a coworker at a utility about whether it better to install each phase of conductors from a distribution substation transformer in its own separate PVC conduit or to put all three phases in one conduit. Generally, we always see each phase plus the neutral in conduits served by our own customer site distribution transformers. 5 sets of cable, 5 conduits. However, this is in a substation application and our operations group wants to utilize three separate conduits )PVC with rigid (ferromagnetic) elbow outside of the substation fence to the UG riser. They want to do this for eas of pulling since it is 1000 mcm cable. They would pull in a ground wire with each conduit. Each conductor has a concentric neutral (1/3rd or 1/9th of phase, not sure). My thought was there could be a problem with heating the elbows since there would be little cancelation of magnetic field for each phase because the other phases would be in conduit 6" and 12" away depending on which phases you are referencing. There would be about 300-400 amps of line current which is about half the peak of the substation transformer. Any comments and references would be welcomed.
thanks
j