JPiii
Mechanical
- Jan 16, 2013
- 6
I am at a plant working on a few product transfer lines. I transfer from building to building crossing out side containment areas. As part of an environmental project, I had automatic valves installed at each building. Before the operator transfers, he must test the line for leaks by charging it for 5 mins. He shuts one valve, pumps until it is full, then shuts the second valve. During our PHA it was determined that we needed Safety Relief Valves on each line. I had these installed which are set to discharge at 165 psi. There are five lines total, of which one relief valve keeps lifting slightly only discharging about a quart of product. I thought it was a bad relief valve so i swapped it for another. That one again lifted. It seems to only be happening in the very beginning of the charge. I removed the failing relief valve and installed a tell-tale pressure indicator on the same flange. The highest pressure shown on the gauge was 70 PSIG. I do not understand, both relief valves were sized for 165 PSIG. The product temperature is about 62 deg C.
I was thinking I needed an expansion tank to absorb the air that could be trapped in the product transfer line when the operator began charging.
But then why is it not shown on the pressure indicator?
Any Ideas?
I was thinking I needed an expansion tank to absorb the air that could be trapped in the product transfer line when the operator began charging.
But then why is it not shown on the pressure indicator?
Any Ideas?