Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Sagging Exterior PSL Deck Beam 1

XR250

Structural
Jan 30, 2013
5,297
I have a project where a 10-year-old exterior 3 1/2x16 PSL beam is sagging. The beam spans 18’-8” and supports 10 foot span floor joists. The beam is measured to be sagging 11/16”. I calculated it should be sagging no more than 5/16” supporting dead load only using a modulus of 1.4E6 per Weyerhauser and including a long-term creep factor of 2. I do not know who actually manufactured this beam, however. I probed the beam and it does not appear to be rotten. As such, I assume it is pressure treated,
About 15 other beams in this townhouse community are sagging similarly.
The sagging echoes what I have seen in other exterior treated engineered beams and have heard anecdotally from other contractors.

I don’t want to be the guy to condemn this beam and then have all the other townhouse owners calling me about theirs. How would y’all proceed? I’m leaning towards doing nothing.
 

Attachments

  • psl.jpg
    psl.jpg
    859.7 KB · Views: 53
Replies continue below

Recommended for you

How does it check out for strength? I've done some FRT and PT wood balcony stuff, from what I remember there are some hefty strength reductions (beyond the incising factor) for engineered lumber.

If it's fine strength-wise, you could chalk it up to creep and excessive deflection, set it up to be monitored periodically and do nothing for now. With a disclaimer that you can't account for continued deterioration. If its blown up, that answers it. It shouldn't too crazy difficult to replace.
 
D/C is about 50% so strength is fine.
"you could chalk it up to creep and excessive deflection"
How do you chalk it up to this? Why is the creep and deflection greater than calculated?

Thanks.
 
The fibers seem to be delaminating, which could indicate longitudinal shearing which may be contributing to the increased deflection. Weather damage might be a factor.


I’d exercise caution. Without conducting a proof test, I wouldn’t approve it.

IMG_0480.jpeg
 
Good call, Tomfh.
Probably cheaper to replace than test.
 
I thought most PSL beams weren't supposed to be used in exterior conditions.
 
Yeah, the glue is probably failing.
 
I thought most PSL beams weren't supposed to be used in exterior conditions.
Pressure treated PSL beams and columns are readily available. They have reduced design values though compared to non-treated ones.
I'll give Weyerhauser a call today and report back.
 
I would never use an EWP for exterior use unless it was fully sealed. The adhesives are vulnerable to temperature, moisture and UV. I've been trying to get Weyerhauser to tell me a safe temperature range for along time. Generally I will only install composites on interiors. Big exception is GLB but I have pretty detailed instructions for exterior use with flashing and sealing.

Here's Weyerhausers thing on moisture https://www.weyerhaeuser.com/woodproducts/document-library/document_library_detail/tb-112/

I don't necessarily know if the PT is actually meant for exterior service or if it's for higher risk service like a crawl space subject to flooding, direct installation on concrete or maybe to ward off pests.

Other weird material things I've found:

- GLB and LVL do much better than strand products in exposed uses.
- Don't let architects fly your glb beams past the roof/sealed deck line without serious capping. They break down over 5-10 years and become a rot path.
- PT is not a good exterior choice in dry environments or environments with big humidity/temp/sun exposure differences by season.
- Box frame pedestals around a column are a bad practice. It's not a matter of if it will destroy the column but when.
 
FWIW, Weyerhauser thinks this may be their beam. They are going to send a sales rep out to take a sample to test if it is treated. If so, they said they will replace it. '
Funny - apparently, they peruse this forum as when I called them they said were expecting to hear from me.
Unfortunately, my XR250 cover has now been blown :)
I have been really impressed with their help on this issue.
 
FWIW, Weyerhauser thinks this may be their beam. They are going to send a sales rep out to take a sample to test if it is treated. If so, they said they will replace it. '
Funny - apparently, they peruse this forum as when I called them they said were expecting to hear from me.
Unfortunately, my XR250 cover has now been blown :)
I have been really impressed with their help on this issue.
See if you can get a service temperature range from them! I've tried a few times over the years and never really got an answer.
 
I've always had good luck with Weyerhauser support. Report back with what you find out.
 

Part and Inventory Search

Sponsor