Under relay settings for 50 , I see two settings 50a,50b
50Na and 50Nb, what are these parameters represent?
50Na and 50Nb, what are these parameters represent?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
It must be the customer's designation for separate overcurrent elements. There are six 50 phase (pickup settings 50P1P, 50P2P...) and also six 50 neutral ground elements (pickup settings 50N1P, 50N2P...). There is only one 3Ø 51 phase element. All six phase elements operate from the same current input. You have to look at the logic settings to determine what is being done with the different elements.Well, I guess there are two settings for instantanious over crrent settings for phase and ground. 50a and 50b.
These are settings that customer set their relay at,so it maybe their own designation type. the values are
50a:3840
50b:640
51:640
50Na:3840
50Nb:900
50N:400
But don't get the 50Nx elements confused with the 50Gx elements
Just a guess: There is a 67P1D set that makes 50b a definite time element. The definite time setting allows coordination with downstream devices, maybe on the secondary side of some large transformers, with shorter time than an inverse characteristic would allow. 50a Hi set trips instantaneously for close-in faults.Yes they are , the values for
50P1P=50b=640
50P2P=50a=3840
there is a 50P3P which is not used anywhere( at least i cant find it).
So what are these two values ( 51B and 51a) represent. I know that they have defined 50a as Hi set instantanious, what about 50b ?
This seems to match the Schweitzer convention except for the SEL-321.Suffix "N" is generally used in preference to "G" for devices connected in the secondary neutral of current transformers, or in the secondary of a current transformer whose primary winding is located in the neutral of a machine or power transformer, except in the case of transmission line relaying, where the suffix "G" is more commonly used for those relays which operate on ground faults.