I have an EOR that is calling for a precast roof in an SDC D structure to be built with prestressed slabs and no topping. The inside dimensions of the building are 114' x 30' with no interior walls. That gives a span to depth ratio of 3.8:1.
The documents show schematic shear plate joint connections with a note stating "FOR REFERENCE ONLY. ACTUAL PRECAST DESIGN AND DETAIL MAY VARY DESIGN OF CONNECTIONS BY PRECAST MANUFACTURER"
That drops the responsibility of the design on me as the Precast SSE. I responded in an email that as follows
[ul]
[li]Per ACI 318 R12.5.3.6 “This Code does not provide provisions for untopped diaphragms assigned to SDC D, E or F." Based on this, I do not know of a way to not have a cast-in-place topping unless there is some provision that I am unaware of.
[li] Section 18.12.6 states that the topping slab must be 2” thick if composite with the precast or 2.5” minimum if not composite. Based on past experience I feel we will be at least 2.5” thick. If we can use composite action with the precast that can be helpful.[/li]
[li] Preliminary design indicates that an 8” solid slab with 2.5” cast-in-place topping will work.[/li]
[/ul]
They came back with a comment about a new provision in the ACE 550.5 for untopped diaphragms in D, E & F but my old 2018ACI Collection does not have 550.5.
Do any of you know anything about this new procedure? The comments on 318 R18.12.11.1 do not make it sound like a very good idea.
The documents show schematic shear plate joint connections with a note stating "FOR REFERENCE ONLY. ACTUAL PRECAST DESIGN AND DETAIL MAY VARY DESIGN OF CONNECTIONS BY PRECAST MANUFACTURER"
That drops the responsibility of the design on me as the Precast SSE. I responded in an email that as follows
[ul]
[li]Per ACI 318 R12.5.3.6 “This Code does not provide provisions for untopped diaphragms assigned to SDC D, E or F." Based on this, I do not know of a way to not have a cast-in-place topping unless there is some provision that I am unaware of.
[li] Section 18.12.6 states that the topping slab must be 2” thick if composite with the precast or 2.5” minimum if not composite. Based on past experience I feel we will be at least 2.5” thick. If we can use composite action with the precast that can be helpful.[/li]
[li] Preliminary design indicates that an 8” solid slab with 2.5” cast-in-place topping will work.[/li]
[/ul]
They came back with a comment about a new provision in the ACE 550.5 for untopped diaphragms in D, E & F but my old 2018ACI Collection does not have 550.5.
Do any of you know anything about this new procedure? The comments on 318 R18.12.11.1 do not make it sound like a very good idea.