Buckeye46
Electrical
- Jun 23, 2018
- 20
A little too eager to wait until Monday when the protection engineers get back to work so I figured I would see what this forum knows about an issue we had on Friday with a 230/60kV transformer. It is brand new, has been in service for over two weeks through high and low load. Friday the generation plant that's off of this substation opens a remote breaker that forces all load to go into my substation and thru parallel banks, one of them being the one in question. As soon as that occurred, the SEL 587 tripped on an 87A. I am attaching images of the event reports. They don't make any sense. I could type an essay in here but I guess I will see if anything jumps out to you guys as to why this occurred. The primary CT waveform does look like its almost clipping.. but CT saturation shouldn't be an issue since it wasn't near its rated capacity by any means. Nor was it fault level current. The restraint and operate currents are pegged at 0.5 which makes no sense to me. Any ideas?