SEL 651 indicator light showing open when closed.

King716

Electrical
Nov 19, 2024
1
SEL 651 Indicator light showing open when closed. Is this a programming issue or something inside the relay itself?
 
Replies continue below

Recommended for you

It's either a programming issue or you are connecting a "b" contact to the relay input instead of an "a" contact.
 
The LED should be programmable, so it was connected to a "b" contact you could change the logic to suit.
 
Is this a new install or has the operation changed?
That is; ws this working properly at one time?
If so look for a bad connection, broken wire or faulty contacts.
Check the relay operation with a jump wire at the relay input terminal, if possible.
 