Tuesday at 3:27 PM #1 K King716 Electrical Nov 19, 2024 1 SEL 651 Indicator light showing open when closed. Is this a programming issue or something inside the relay itself?
SEL 651 Indicator light showing open when closed. Is this a programming issue or something inside the relay itself?
Tuesday at 5:35 PM #2 jghrist Electrical Jul 16, 2002 4,212 It's either a programming issue or you are connecting a "b" contact to the relay input instead of an "a" contact. Upvote 0 Downvote
It's either a programming issue or you are connecting a "b" contact to the relay input instead of an "a" contact.
Tuesday at 5:52 PM #3 System Protection Electrical Apr 13, 2023 44 The LED should be programmable, so it was connected to a "b" contact you could change the logic to suit. Upvote 0 Downvote
The LED should be programmable, so it was connected to a "b" contact you could change the logic to suit.
Tuesday at 6:04 PM #4 waross Electrical Jan 7, 2006 26,872 Is this a new install or has the operation changed? That is; ws this working properly at one time? If so look for a bad connection, broken wire or faulty contacts. Check the relay operation with a jump wire at the relay input terminal, if possible. Upvote 0 Downvote
Is this a new install or has the operation changed? That is; ws this working properly at one time? If so look for a bad connection, broken wire or faulty contacts. Check the relay operation with a jump wire at the relay input terminal, if possible.
Wednesday at 10:01 AM #5 LittleInch Petroleum Mar 27, 2013 21,342 One of these? https://selinc.com/products/651R/ Item 7 says its software programmable, so check the software. how do you know its actually closed? Upvote 0 Downvote
One of these? https://selinc.com/products/651R/ Item 7 says its software programmable, so check the software. how do you know its actually closed?