Keith 1, which boring logs did you review? I think the best and possibly the only reliable log is of boring PB-1 drilled by Slate near the two indicator pile locations on Fremont Street. It shows Franciscan Melange from 256 feet down to 323 feet. The melange is described by Slate as "generally consists of pervasively sheared shale matrix supporting blocks of siltstone, sandstone, chert, serpentinite, and volcanics; blocks vary from 1/2 to 3 inches; local serpentinite and quartz veins." There is no indication of even a rather weak shale base. The melange is known to be a tricky material that can vary quite widely over short distances. Not what I would want to support a 600-foot tall, concrete-framed building. Ron Hamburger, a structural engineer, keeps on referring to piles drilled into rock, but this is not what most geotechnical engineering would regard as rock for this purpose. It is instructive to see what Slate wrote about the first indicator pile, which they abandoned because they could not keep the hole open: "leaving the uncased rock socket hole open for any significant amount of time, as well as repeated extraction and re-insertion of the drilling tooling and flushing with water, seems to be detrimental to the stability of the hole [which should not have been a surprise!]. The Franciscan Complex bedrock materials are quite variable ..."
Thank you for your support of good geotechnical / civil engineering!
But also, the one and only "pile load test” was done on the second indicator pile which had three Osterberg load cells embedded in the rock socket plus other devices to measure deformation. They do some tricky stuff to come up with “unit side shear resistances”. That is all they report, but I added up the shear forces around a 2-foot diameter pile and got 663 kips in the Lower Alameda formation and 2060 kips in the Franciscan. These are not capacities of any kind – just what was developed when the load cells reached their limit of 800+ kips. So, if you believe this, you could safely apply 1000 kips as a permanent load. But I think there is something funny about these numbers. The loads cells, when tested one at a time maxed out pushing a bit over 800 kips in both directions, up and down, 1600 kips total. I am not sure how they then get interpreted resistances that add up to 2723 kips (not my expertise and I don't have time to read all the relevant literature). Also, the capacity for a downwards load might be different because of a different pattern of deformation and the long-term capacity of the Franciscan Melange might be different from the short-term capacity. Basically a lot of unknowns. To rely on just one pile load test and some input from adjacent sites (which John Egan mentioned in his remarks to the Board of Supes hearing) seems like more than a bit of a gamble for a high-profile fix and building.