Smart People,
I’m working on renovation of 3-story c1927 house (unfinished walkout basement, street and upper level finished, 30 ft x 30 ft footprint). Basement is to be finished, including lowering by 18in (underpinning) to increase ceiling height from 6ft 8in to 8ft 0in (incl flooring).
House has central chimney. Chimney footing appears to rest on 2ft to 4ft of ML / sandy clay loam native soil over deep SP / loamy sand native soil (40ft + likely - based on familiarity with soils local to site). The seasonal high water table is probably 20ft + below footing.
Numbers I’m working with are:
DL_chimney: 46kips
DL_foor: 15kips (appears chimney acts as structural column - assessment phase)
LL_floor: 45kips (as above)
DL+LL: 106 kips
q_a: 2000psf (prescriptive bearing capacity)
A_fe: 20.4sf (existing footing)
So, A_fr = (106E3lb)(1sf/2000lb) = 53sf (required footing)
A_fe/A_fr = 0.38sf/sf (38%) ... required footing area significantly less than existing
I’m tracking this is all simplistic prescriptive bearing capacity (possibly 3x +/- safety factor) and without regards to expected / potential / allowable settlement.
I plan to check soils during underpinning excavation to adjust footing design as required, but I’d rather not disturb existing conditions unnecessarily.
So, question is ... after 94 yrs, is there any practical reason to expect footing area needs to be increased beyond existing if there is no foreseeable increase of DL/LL?
Any and all input appreciated!