I am designing the anchor rods for a pre-engineered metal building. The PEMB engineer placed x-bracing in the end walls. For the load case with wind load parallel to the frame, they are giving me shear parallel to the frame from the x-brace and shear perpendicular to the frame from sidewall pressure. In total I have and tensile force of roughly 12 kip, a shear force parallel to the wall equal to roughly 9 kip, and a shear force perpendicular to the wall equal to roughly 11 kip. My columns are sitting on pedestals with limited edge distance, so supplementary reinforcement is required for all three cases.
The code requires an interaction ratio equal to or less than 1.2. In this case, would it be appropriate to use Nu/φNn + Vuparallel/φVnparallel + Vuperp/φVnperp < 1.2? This may be overly conservative for the steel strength itself. With checking the steel for shear, I may use Vu equal to the resultant shear. I’m not sure how I would combine this with tension, however. Any thoughts?
The code requires an interaction ratio equal to or less than 1.2. In this case, would it be appropriate to use Nu/φNn + Vuparallel/φVnparallel + Vuperp/φVnperp < 1.2? This may be overly conservative for the steel strength itself. With checking the steel for shear, I may use Vu equal to the resultant shear. I’m not sure how I would combine this with tension, however. Any thoughts?