shear transfer to concrete via shotpins?

Status
Not open for further replies.

cruzinbear

Structural
Dec 19, 2012
19
Are there any shotpins (or similar) in the market, with an available ESR report, to transfer seismic shear forces from shear wall (down to cold-form steel tracks) to concrete slab of self-suported structure?
 
Replies continue below

Recommended for you

Hi Cruzinbear,

Typically our firm has used Hilti X-U pins for a situation similar to what you describe when the walls are fairly lightly loaded. Please note that we have not used them for a designated seismic system, only R=3 systems so far (I think that seismic testing was specifically out scoped in the reports linked below).

ICC ES Reports:


You also may want to check this out:


Good luck!

-Huck
 