A 6'x6' entry addition to an existing single story wood framed structure has been constructed. Now I have been asked to show that this is adequate for wind loads.
Here is the plan:
____________________
| |
| |
|_ _|
There are no openings on the sides; a 3' wide door occurs in the front wall (opposite the original building). Walls are 8' high, 2x4@16" o.c., fully sheathed with structural panels. Floor is slab on grade. Code is 2006 IBC. Seismic Design Category A.
IBC 2308.9.3 requires braced wall panels at least 48" wide at each end; I only have 18" each side of the door.
IBC 2308.9.3.1 allows 2'-8" panels; I only have 18"
IBC 2308.9.3.2 allows 16" panels, but the header must be at least 6' between panels; I would only have 3'-4" between the 16" panels.
So I give up on "Conventional Light Frame Construction"
IBC 2305.3.4 limits the aspect ratio of a shear wall pier to 3.5:1; Each side of the door is 8 ft./1.5 ft. = 5.3:1
Trying a perforated shear wall doesn't work: 2305.3.5.1 defines the height of the perforated shear wall segment to be the same as the shear wall pier.
Assuming I could make the roof work as a diaphragm (the entry has a cathedral ceiling) to get the load back into the original building doesn't pass either….IBC 2305.2.5 limits the length of a cantilevered diaphragm to 2/3 of the diaphragm width, so the maximum cantilever permitted is 4 feet; I have 6.
This is a simple wood box, with a hole in one side. There are countless "tool sheds" built to a lesser construction that have been standing for ions. It can't be this hard…..help!!
Here is the plan:
____________________
| |
| |
|_ _|
There are no openings on the sides; a 3' wide door occurs in the front wall (opposite the original building). Walls are 8' high, 2x4@16" o.c., fully sheathed with structural panels. Floor is slab on grade. Code is 2006 IBC. Seismic Design Category A.
IBC 2308.9.3 requires braced wall panels at least 48" wide at each end; I only have 18" each side of the door.
IBC 2308.9.3.1 allows 2'-8" panels; I only have 18"
IBC 2308.9.3.2 allows 16" panels, but the header must be at least 6' between panels; I would only have 3'-4" between the 16" panels.
So I give up on "Conventional Light Frame Construction"
IBC 2305.3.4 limits the aspect ratio of a shear wall pier to 3.5:1; Each side of the door is 8 ft./1.5 ft. = 5.3:1
Trying a perforated shear wall doesn't work: 2305.3.5.1 defines the height of the perforated shear wall segment to be the same as the shear wall pier.
Assuming I could make the roof work as a diaphragm (the entry has a cathedral ceiling) to get the load back into the original building doesn't pass either….IBC 2305.2.5 limits the length of a cantilevered diaphragm to 2/3 of the diaphragm width, so the maximum cantilever permitted is 4 feet; I have 6.
This is a simple wood box, with a hole in one side. There are countless "tool sheds" built to a lesser construction that have been standing for ions. It can't be this hard…..help!!