I have run into a situation where the contractor has installed 400 headed stud anchors to be 4" long with a 3" composite metal deck and 2" of concrete over the deck. This gives 1" projection over the metal deck. They were supposed to install 4 1/2" length to get the minimum 1 1/2" projection that AISC calls for.
AISC Section I3.2c(1)(2) states: “Steel headed stud anchors, after installation, shall extend not less than 1½ in. above the top of the steel deck and there shall be at least ½ in. of specified concrete cover above the top of the steel headed stud anchors.”
However, Section 1.11.6 stated: “When composite construction does not conform to the requirements of Sects. 1.11.1 through 1.11.5, allowable load per shear connector must be established by a suitable test program.”
The question is, does anyone know of a suitable test program that could help me evaluate the capacity of these shear stud anchors that are too short? I would really prefer to tell the contractor that he only needs to add a few anchors to make up for the reduced capacity vs telling them to uninstall all of them and reinstall.
AISC Section I3.2c(1)(2) states: “Steel headed stud anchors, after installation, shall extend not less than 1½ in. above the top of the steel deck and there shall be at least ½ in. of specified concrete cover above the top of the steel headed stud anchors.”
However, Section 1.11.6 stated: “When composite construction does not conform to the requirements of Sects. 1.11.1 through 1.11.5, allowable load per shear connector must be established by a suitable test program.”
The question is, does anyone know of a suitable test program that could help me evaluate the capacity of these shear stud anchors that are too short? I would really prefer to tell the contractor that he only needs to add a few anchors to make up for the reduced capacity vs telling them to uninstall all of them and reinstall.