Short Rebar Splices

Status
Not open for further replies.

learning2geotech

Civil/Environmental
Apr 4, 2019
41
If I have short overlap between two rebars,i.e 10" instead of the proposed 24",can I add another section of rebar, same size, say 8ft long, to the overlapping area?
 
Replies continue below

Recommended for you

Provide a sketch to confirm what you are asking. Generally, yes you can have a third bar (if it has adequate splice length to each of the other 2 bars that are partially lapped) that provides the required splice length. Usually this may be done for constructability reasons, such as avoiding really long bars with hooks.
 
I think you need a 4' bar centered on the bar to be spliced.
 

They're 55M bars and have to be 10' long (WAG)[bigsmile]. The splice length is dependent on the tensile development length, hence the bar size.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?
-Dik
 