Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

SHRINKAGE CALCULATION OF CONCRETE 1

Status
Not open for further replies.

Tstruct

Structural
May 14, 2023
87
0
0
PK
Hello,
I have to provide a plain concrete mass to make a trench for cables. Length of this trench is 15'. Sectional dimensions can be seen below.
PLAIN_CONC_gsw9n6.jpg


What I am concerned about is whether there be enough shrinkage in this 15' long mass of concrete to develop cracks?
How can I check it? What would be the permissible limits and precautions?
 
Replies continue below

Recommended for you

I wouldn't bother trying to calculate that. Re-entrant corners are crack magnets. You can chamfer the corners to eliminate the 90-degree angles and/or add a diagonal rebar behind each corner like is commonly found around openings in walls.
 
Is there anything restraining it from shrinking? If it’s a 15 ft long chunk of concrete free to shrink without restraint, cracking should be minimal.
 
Whether it cracks depends on the degree of restraint.

You might get away with it.

I don’t think it warrants being fully reinforced but a layer of mesh 6” off the bottom wouldn’t be a bad idea.
 