shunt reactors

Status
Not open for further replies.

abdulelahY

Electrical
May 13, 2012
3
I have some work on shunt reactors
i know it is used Because of rise of voltage,
i need to know where use it specifically ?
how much miles to use it with head line ? , and how much MVAr need?
for capacitive rise the same questions ?

i need rule for how mutch i need reactor with ultra voltage and EHV .
 
Replies continue below

Recommended for you

You have to do studies of power system : energization of unload transmission line by EMTP , and/or power flow to control reactives
 
odlanor

first thank you,
actully I do study it , but the study give general idea only [sad] like :
1- feranti effect it cuse cause rise of voltage for line longer than (150) miles .
2- capacitive rise .
3- use reactor on line , and it is Possible on busbar.

but how to do calculation for it ???
like you have a system 380 KV a long distance it is coming to substaction
here shunt reactor is needed as general , but how match MVAr you need by calculation ???

this is something did not find in books [sad] !!!



 
If you need Xr ohms of shunt reactor to reduce Ferranti effect
so you need a shunt reactor of 380*380/Xr MVAr.
Power system analysis - Hadi Saadat 5.9.1 line compensation-shunt reactors.

Ferrant effect is a temporary overvoltage.You need also to study switching surge voltage by EMTP or ATP during line energization.
 