- May 6, 2009
- 56
We had a pump station rebuilt last fall. The Plant manager decided to shut power to the building off during the winter.
Two circuit breakers in the mcc had problems upon start up last week. One of the breakers started working after the handle was operated many times. The other breaker was replaced.i opened up the bad breaker to find lots of corrosion inside as well as evidence of a nice arc flash.
We are located in New Hampshire so the temp in that building got down to around zero.
This pump station is critical during the dry summer months.My concern is the other breakers in the mcc being corroded also.
My report to the plant manager is going to state that we need to keep this building heated during the winter months and i am suggesting that a tech from the mcc manufacturer come look at the remaining breakers. This is 1600a 480v switchgear and i am concerned that this gear will not be reliable when needed and that the danger of arc flash is increased because of internal corrosion of the breakers.
any thoughts?
this breaker was NEW 6 months ago. the picture is bad but you can see the arc burn and the corrosion
Two circuit breakers in the mcc had problems upon start up last week. One of the breakers started working after the handle was operated many times. The other breaker was replaced.i opened up the bad breaker to find lots of corrosion inside as well as evidence of a nice arc flash.
We are located in New Hampshire so the temp in that building got down to around zero.
This pump station is critical during the dry summer months.My concern is the other breakers in the mcc being corroded also.
My report to the plant manager is going to state that we need to keep this building heated during the winter months and i am suggesting that a tech from the mcc manufacturer come look at the remaining breakers. This is 1600a 480v switchgear and i am concerned that this gear will not be reliable when needed and that the danger of arc flash is increased because of internal corrosion of the breakers.
any thoughts?
this breaker was NEW 6 months ago. the picture is bad but you can see the arc burn and the corrosion