A little off topic but...
When a system is operating, subcooled liquid enters and exits the receiver quicker than the pressure and temperature can achieve an equilibrium. The liquid/vapour interface is the only location where saturated conditions exist. This is why when you measure the outlet temperature of a receiver it is almost always subcooled; in reality, most of the receiver is full of subcooled liquid if the unit is operating properly. Some systems do bypass liquid to gain some efficiency, particularly if they have mechanical subcooling.
As imok2 said, a sightglass is used to determine whether a solid column of liquid is present in the liquid line. This helps in troubleshooting many problems such as refrigerant charge, lack of subcooling, plugged filter/driers... etc