I am reviewing a design that has a beam subjected to 200k-ft max moment and a 32 ft span, the designer has specified a W21x44. When I checked the beam via ASD the compressive flange would have to be braced at least every 4.7-ft to meet the flange criteria. I think the designer is just selecting the beam by Mr method without checking the unbraced length. Am I interpreting this correctly?