"It's a single phase with internal temp tripping, so probably not so much."
That thermal protection device is mass produced. It will generally protect a motor from the first jam-up, but if a motor is left jammed and cycling on auto resetting thermal protection, all bets are off.
When I was working in the turd world a power outage every Sunday for maintenance was common. There was a combination of four wire wye:delta transformer banks and single phase switching when the power was restored.
This put about 50% voltage on two thirds of each residential circuit until the second phase was closed.
All of the refrigerators and freezers had been without power for several hours and tried to start. With 50% voltage they all stalled.
The thermal protection would cut out shortly after full voltage was restored, but every weekend, somewhere in town, one or two hermetic compressor motors would fail. This was popularly attributed to "Power Surges".
Thermal protection is good but not perfect.
Small protection devices were available and common. The protection combined a voltage monitoring circuit which cut off the output if the voltage was too low or too high and a three minute timer before re-energizing.
A couple of shorted turns may give the observed symptoms for a short while before total failure.
Bill
--------------------