ThePunisher
Electrical
- Nov 7, 2009
- 384
Hi all,
I would like to place this Query(s), though this might be an old-long discussion.
I am currently looking into an electrical load list to size "new" MCC and another to assess "existing" MCC.
The electrical load lists have a summary of three loading categories, Continuous, Intermittent and Peak. The MCCs (and switchgears, transformers) are sized based on PEAK loading.
The Maximum "Running" loading is based on (100% x Continuous Loads) + (30% x Intermittent Loads), where 30% is the factor of intermittency and is variable based on engineering judgment.
The PEAK loading, on the other hand, is based on (100% x Continuous Loads) + (30% x Intermittent Loads) + (10% x Standby Loads), where again, 30% is the factor of intermittency and 10% is the standby factor used, both variable based on engineering judgment.
I would like to question the 10% standby load added into the peak loading, which in turn is used for sizing the MCC bus rating. If these standby loads are only used for operational reliability and are only switch on if the other motor is off (like in the case of motors A and B, or MOVs used to open/close only...not throttling), is the "standby" loads added to the peak make any sense. Even if, say the "B" motor is started first before "A" motor is switched off, this loading will only take less than 10 seconds to start and overall less than 20 seconds for both running, can this be a good justification to say make them part of equipment sizing.
The problem is that when I have significant "standby" loads in one MCC, their 10% contribution to the peak load can be substantial. This becomes critical when evaluating loading of an existing MCC wherein taking 10% standby would make the result almost borderline.
Can anyone here help me out in case, I am missing something or misunderstood the concept.
Thank you in advance.
I would like to place this Query(s), though this might be an old-long discussion.
I am currently looking into an electrical load list to size "new" MCC and another to assess "existing" MCC.
The electrical load lists have a summary of three loading categories, Continuous, Intermittent and Peak. The MCCs (and switchgears, transformers) are sized based on PEAK loading.
The Maximum "Running" loading is based on (100% x Continuous Loads) + (30% x Intermittent Loads), where 30% is the factor of intermittency and is variable based on engineering judgment.
The PEAK loading, on the other hand, is based on (100% x Continuous Loads) + (30% x Intermittent Loads) + (10% x Standby Loads), where again, 30% is the factor of intermittency and 10% is the standby factor used, both variable based on engineering judgment.
I would like to question the 10% standby load added into the peak loading, which in turn is used for sizing the MCC bus rating. If these standby loads are only used for operational reliability and are only switch on if the other motor is off (like in the case of motors A and B, or MOVs used to open/close only...not throttling), is the "standby" loads added to the peak make any sense. Even if, say the "B" motor is started first before "A" motor is switched off, this loading will only take less than 10 seconds to start and overall less than 20 seconds for both running, can this be a good justification to say make them part of equipment sizing.
The problem is that when I have significant "standby" loads in one MCC, their 10% contribution to the peak load can be substantial. This becomes critical when evaluating loading of an existing MCC wherein taking 10% standby would make the result almost borderline.
Can anyone here help me out in case, I am missing something or misunderstood the concept.
Thank you in advance.