ExxonMobil std. XVD said:
Acoustically Induced Vibration Problems in Header Systems
Large headers inherently have the potential for flow induced vibration problems. In particular, flare headers for gas piping systems in which high capacity pressure reducing valves discharge have experienced problems of fatigue failure where excessive turbulence and high acoustic energy existed. The turbulent forces excite complex modes of vibration in downstream piping components. These vibrations can in turn result in stresses exceeding the endurance limit for the materials and thus, fatigue failure. Pressure relief devices may have the capability of generating sufficient acoustic energy to cause fatigue failures in downstream discharge laterals and/or header piping.
Potential vibration problems of this type should be considered early in the design stage of the header system. Guidelines for assessing the potential of acoustically induced piping vibrations in pressure reducing systems are contained in the Piping Vibration Evaluation Guide, EE.21E.89 (Section 7).
1. The following screening criteria should be used to recognize services with potential vibration problems requiring further detail evaluation:
a. Downstream line size 16 in. (400 mm) and greater: mass flow rate greater than 200,000 lb/hr (91,000 kg/hr) or upstream to downstream pressure ratio greater than 3.
b. Downstream line size 8 to 14 in. (200 to 350 mm): downstream line velocity greater than 50% sonic and upstream to downstream pressure ratio greater than 3.
c. Downstream line size less than 8 in. (200 mm) swaged up or “Teed" to 8 in. (200 mm) or larger line: downstream line velocity greater than 50% sonic and upstream to downstream pressure ratio greater than 3.
The above criteria are a guide for detecting potential problems with gas letdown systems and apply for the piping downstream of the pressure reducer under concern. Systems with only liquid flow are not identified as potential problems and need not be investigated. For systems with two-phase flow, use the conservative assumption of the total mass flow rate as gas. Any system exceeding these criteria should be further evaluated in accordance with the guidelines and calculation procedures set forth in the Piping Vibration Evaluation Guide, EE.21E.89 (Section 7). It is further recommended that the Mechanical Engineering Services Section of EETD be consulted when a piping system problem is suspected.
A distinction must be made regarding the length of service of the pressure reducing systems. Fatigue failure of any mechanical system depends on time, i.e., the number of cycles to failure. Therefore, the treatment required for a continuous service may not be justified for a short-term service.
2. Short Term Service - A system in short-term service is defined as one which operates a total of 12 hours or less during the life of the plant. Pressure relief devices typically do not exceed this limit. Systems in short-term service exceeding the screening criteria indicated above should be evaluated in accordance with EE.21E.89. Services determined from this evaluation to require special treatment should be identified as follows in the Design Specification:
Notes for Design Specification - The following design features should be applied to the discharge piping and header for approximately 300 ft (90 m) downstream from the PR device in question. (A more rigorous distance formula based on acoustic power level is given in EE.21E.89.)
a. Use pipe with a minimum wall thickness of 1/2 in. (13 mm) to increase flexural stiffness.
b. Use completely welded full wrap-around reinforcement pads at branch connections per ASME B31.8, Figure 13, Sleeve Type, with pad thickness equal to header wall thickness.
c. Use wrap-around reinforcement at welded support shoes and anchors. Alternatively, all welding of these fittings to the pipe wall may be eliminated by the use of bolted shoes and anchors.
d. Minimize all vents, drains, and small diameter connections. Those remaining must be double gusseted.
3. Continuous Service - Pressure reducing valves which will be operated more than 12 hours during the life of the plant should be considered to be in continuous service. Such systems, which exceed the screening criteria given herein, should be further evaluated in accordance with EE.21E.89. Systems in continuous service believed to be fatigue prone per EE.21E.89 require more positive action to reduce the acoustically induced vibrations because of the greater potential for fatigue failures in these systems. Treatment alternatives for these services typically require measures to reduce the acoustic energy generated at the source. The Mechanical Engineering Section of EETD should be consulted when problems of this type are suspected.
4. Maximum Line Velocity - Sonic conditions at piping discontinuities such as at branch connections, reducers, etc., can also result in unacceptable acoustically induced vibrations. Maximum vapor or mixed phase flow velocities in piping should not exceed 50 percent of sonic for releases expected to exceed 12 hours during the life of the plant or 75 percent of sonic for releases having a lower cumulative duration (such as pressure relief valve releases).
Design for Startup Conditions - Closed headers must be designed for any abnormal conditions that may exist during commissioning of the header or plant startups.