Hi All,
I have a commercial project where an existing slab on grade will be replaced with a new 5" concrete slab, reinforced with #4 @ 12" O.C. each way. The concrete mix is 4000 PSI concrete with 25% flyash. The contractor wants to use the slab as soon as possible to perform the remodel construction. There will likely be forklift traffic (weight unknown right now) which will be carrying steel beams during construction. We told him 3 days cure time before using the slab. The contractor is wondering if there is a target concrete break strength and if there is a possibility to continue with construction any earlier.
Does anyone have any good advice for this situation? I'm thinking that the contractor should use a mix without flyash to attain higher early concrete strength. I'm wondering if using an accelerator would be suitable in this situation, but the concrete will be exposed so I'm worried if the accelerator will cause any finishing issues or other unforeseen issues. 3 day strength of a 4000 PSI mix is roughly 40% = 1600 PSI. Using different analysis methods, this strength seems adequate for heavy point loads, and strengths as low as 1000 PSI seem adequate also.
Here's my summary:
I don't think it's a good idea to use the slab prior to 3 days cure time with conventional concrete. Target strength prior to using the slab shall be +/- 1500 PSI. I don't think using a 5000 PSI or higher mix will help attain that strength in less than 3 days. I'm unaware of the consequences of using a chloride-free concrete accelerator.
Thoughts anyone?
I have a commercial project where an existing slab on grade will be replaced with a new 5" concrete slab, reinforced with #4 @ 12" O.C. each way. The concrete mix is 4000 PSI concrete with 25% flyash. The contractor wants to use the slab as soon as possible to perform the remodel construction. There will likely be forklift traffic (weight unknown right now) which will be carrying steel beams during construction. We told him 3 days cure time before using the slab. The contractor is wondering if there is a target concrete break strength and if there is a possibility to continue with construction any earlier.
Does anyone have any good advice for this situation? I'm thinking that the contractor should use a mix without flyash to attain higher early concrete strength. I'm wondering if using an accelerator would be suitable in this situation, but the concrete will be exposed so I'm worried if the accelerator will cause any finishing issues or other unforeseen issues. 3 day strength of a 4000 PSI mix is roughly 40% = 1600 PSI. Using different analysis methods, this strength seems adequate for heavy point loads, and strengths as low as 1000 PSI seem adequate also.
Here's my summary:
I don't think it's a good idea to use the slab prior to 3 days cure time with conventional concrete. Target strength prior to using the slab shall be +/- 1500 PSI. I don't think using a 5000 PSI or higher mix will help attain that strength in less than 3 days. I'm unaware of the consequences of using a chloride-free concrete accelerator.
Thoughts anyone?