Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Smaller dt Hint Message

Status
Not open for further replies.

amicka

Civil/Environmental
Aug 2, 2005
18
We're trying to replicate the work done in an older version of HydroCAD using version 9.00. We are getting message 49 "Hint: Tc<2dt may require smaller dt" for one of our subcatchments. The Tc is 5.8 minutes.

Our dt was set at 0.50, which we reduced to 0.10, but the message remains.

What do we need to change to satisfy the program and get rid of this message? Or is this something that should not concern us?
 
Replies continue below

Recommended for you

Usually, if the dt is 1/2 of the smallest Tc or less, the error should not come up. There is a possibility that your minimum Tc is set greater than 5.8 minutes. You can change this in Settings -> Calculation -> Advanced, but this is usually a different error message.
 
The default dt of 0.05 hours is suitable whenever the Tc is 0.1 hours (6 minutes) or greater. For a smaller Tc you will get hint 49, suggesting a smaller dt. (Be sure to click the message for full details!)

For your Tc of 5.8 minutes, reducing the dt to 0.04 hours will eliminate the message.

Note: The "Minimum Tc" setting is used to arbitrarily raise any Tc that falls below the specified threshold. This feature is intended for use ONLY when a minimum Tc is prescribed by local regulations. Otherwise the actual Tc value should be used.

For further information please see

Peter Smart
HydroCAD Software
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor