Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Snow accumulation around elevated mechanical unit

Status
Not open for further replies.

MALKOBANI

Structural
Oct 16, 2006
21
0
0
Hi all,

When calculating snow accumulation, do you consider a mechanical roof unit elevated by 1.2m stub-columns same as if it is not elevated ?

Thanks to your input
 
Replies continue below

Recommended for you

I would normally consider it having a height of 1.2m plus the height of the mechanical unit. In addition, in Canada, there is a manner of calculating a snow accumulation around a roof top unit.

Dik
 
Dik:

I understand snow accumulates when wind blows the snow and when snowflakes hit a barrier; they fall and accumulate beside that barrier. In this case the wind can blow under the unit and disperse the accumulated wind. Therefore, I think there should be some reduction in the accumulation.
 
It's not so much the snow hitting the barrier, but the change in wind velocity around obstructions that tends to cause snow to 'precipitate' when the localized velocity is diminished.

Dik
 
Status
Not open for further replies.
Back
Top