Split system question

Status
Not open for further replies.

jvithayapun

Mechanical
Sep 17, 2009
22
Say a split system is rated at 2 tons
Total MBH=24.

Assuming the t-stat is set at 75F and the fan in the unit does 425 cfm.

So:
24000 = ( 425 cfm) * (1.1) * deltaT

Therefore deltaT = 51.33

Does that mean if my room is set to 75, my EAT=75 and my LAT off the coil is (75-51.33)=23.7F? Im trying to see what my LAT would be in this case.

Thanks in advance
 
Replies continue below

Recommended for you

ok,
so if i use
Qt = cfm * 4.5 * deltaH

24000 = 425 cfm * 4.5 * deltaH

deltaH = 12.54

Now assuming EAT=75F at 50% then h=28.15

so 28.15-12.54 = 15.61 = h leaving coil

Im looking for some random point with about 100% saturated air and i am coming up with 25 db/ 25 wb that gives me a h=15.52. so is this the leaving air temperature?
 
disregard last post, i found my error.
the h that gives me 15.52 is roughly 41db/41wb. i believe this would be correct?
 
Well, with a lot of happifying assumptions, sure, maybe.

Just because a system is "rated" at 2 tons doesn't mean it will always provide 2 tons of cooling at the evaporator. In fact, most likely it will very rarely provide that.
 
I think you might be thinking of this wrong or backwards or something. The rating of the unit relates to its ability. A system with mid-range fan pressure drop is typically about 400 cfm per ton (sort of a standard but not too reliable thumbrule); breaks down for very low or high pressure systems…

The Btu/hr is a result rather than an input variable. For example, if your unit is cooling an inlet mixed airstream from 78°F down to 52°F at your given airflow (425 cfm), the unit is providing about 12,200 Btu/hr, or about a ton of cooling. That’s about half its capacity; it has the nuts to handle a lot more load. That’s sensible (Q = 1.1 cfm dT). Total load would be Q = 4.5 cfm dh, where h is in Btu/lbm.

Keep in mind your discharge temperature can’t be below your apparatus dew point (a term I’m not to crazy about because it tries to make HVAC sound like rocket science)—basically your discharge temperature can’t be below the lowest surface temperature of the coil. So to achieve your two ton rating you’d have to put in air that’s about twice as warm or have about twice the airflow.
 