Its about 5 days that Im researching about sprinkler above drop ceiling but I can decide its a mandatory to install sprinkler above drop ceiling or not. In NFPA there are a few clauses about drop ceiling.
8.15.23 Spaces Above Ceilings.
8.15.23.1 Where spaces have ceilings that are lower than the
rest of the area, the space above this lower ceiling shall be
sprinklered unless it complies with the rules of 8.15.1.2 for
allowable unsprinklered concealed spaces.
8.15.23.2 Where the space above a drop ceiling is sprinklered, the sprinkler system shall conform to the rules of
11.1.2 and Section 12.3.
8.15.23.3* Where there is a noncombustible space above a
noncombustible or limited-combustible drop ceiling that is
sprinklered because it is open to an adjacent sprinklered
space on only one side and where there is no possibility for
storage above the drop ceiling, the sprinkler system shall be
permitted to extend only as far into the space as 0.6 times the
square root of the design area of the sprinkler system in the
adjacent space
2016 version of NFPA 13 describes cloud ceilings but the ceilings in my project are not those types. I've read 8.15.1 Concealed Spaces but still cant decide about this subject.
May you help me?
Its about 5 days that Im researching about sprinkler above drop ceiling but I can decide its a mandatory to install sprinkler above drop ceiling or not. In NFPA there are a few clauses about drop ceiling.
8.15.23 Spaces Above Ceilings.
8.15.23.1 Where spaces have ceilings that are lower than the
rest of the area, the space above this lower ceiling shall be
sprinklered unless it complies with the rules of 8.15.1.2 for
allowable unsprinklered concealed spaces.
8.15.23.2 Where the space above a drop ceiling is sprinklered, the sprinkler system shall conform to the rules of
11.1.2 and Section 12.3.
8.15.23.3* Where there is a noncombustible space above a
noncombustible or limited-combustible drop ceiling that is
sprinklered because it is open to an adjacent sprinklered
space on only one side and where there is no possibility for
storage above the drop ceiling, the sprinkler system shall be
permitted to extend only as far into the space as 0.6 times the
square root of the design area of the sprinkler system in the
adjacent space
2016 version of NFPA 13 describes cloud ceilings but the ceilings in my project are not those types. I've read 8.15.1 Concealed Spaces but still cant decide about this subject.
May you help me?